Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Concrete pad for exterior MEP equipment

Status
Not open for further replies.

cmrdata

Structural
Oct 19, 2010
70
I need to provide two separate concrete pads to support an exterior chiller and electric substation. The frost depth in this area is between 2'-6" and 3'.

I have seen different ways to do this:

1. Simply a think concrete pad.
2. Concrete pad with some small diameter(6"?)piers drilled 3 foot deep located at several selected location that tied into the slab above.
3. Concrete pad with all four edges thickened/turned down (3' deep).

I suspect Method 1 assumed that the utility connections are flexible enough to accommodate the vertical movement of the supporting pad caused by freeze and thaw?

I appreciate thoughts anyone might have.

Thanks.
 
Replies continue below

Recommended for you

You could do a partial thickened edge (say 24") sitting on a 12" thick layer of non-frost susceptible soil. You would still end up with some vertical movement but I'm sure it would be a manageable amount.You should check with the chiller supplier and see what kind of movement they can tolerate with their connections.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor