Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Compressive steel 3

Status
Not open for further replies.

DOUS1

Structural
Sep 8, 2010
1
i need help determining the area of compressive steel for a T Beam...i have already found the area of tensile steel. I need to check the beam for strength and ductility and require the area of compressive steel but im new to design and cant seem to find anything in the concrete design codes AS3600. any help would be appreciated...
 
Replies continue below

Recommended for you

If you have already calculated what tensile steel that you need for strength and the section is ductile (i.e. ku is less than 0.4) than you won't require any compressive steel.

Unless you require some compressive steel for service requirements such as deflections.
 
Time to open up "concrete Structures" by warner et al and read the section on doubly reinforced beams, this will get your the baics that you can then apply to t-sections.

An expert is a man who has made all the mistakes which can be made in a very narrow field
 
Dous1

Clause 8.1.5 and a good textbook as suggested above.

AS3600 will not tell you how to calculate a double reinforced member, that is textbook stuff, not code stuff.
 
Status
Not open for further replies.

Part and Inventory Search