celtickid
Structural
- Apr 28, 2008
- 2
I have a series of 32' long girders in a composite floor system that happen to have one end (about 24" lemgth) without a composite slab on both sides of the flange due to a 2 story CMU wall passing through (see uploaded file attachment). Of course RAMSteel will not design the girder as composite but common sense tells me that since most of the member has a composite slab, it could still be designed as composite provided that the beam location at and near the end with the opening is checked as non-composite for the moment at that location. I am a little fuzzy on the horizontal shear aspect though..I realize the horiz. shear gets greater towards the ends of the beam but since the opening is still less than the maximum stud spacing (8 times the slab thickness)everything should be fine. Am I missing something? Does anyone know of a good design example for this?