rcw retired EE
Electrical
- Jul 21, 2005
- 907
I'm helping on an IEC project in Africa and want to know if ungrounded control power is typical for IEC MCC's. MCC's were built in China.
Each 690V MCC has a 690V-230V, single-phase control power transformer that feeds a distribution panel with single pole breakers, one breaker per MCC bucket. The 230V winding is floating ungrounded on four of the transformers and is grounded on two of them. One has the hot leg grounded so the control circuit is still energized when the CB is open. The two grounds appear to be unintentional, (haven't located them yet).
I told the electricians to find and fix the unintentional grounds and then ground the neutral side - the one not connected to the breakers.
Is there a good reason to leave the control power ungrounded? I couldn't come up with one. BTW there is no ground detection circuit.
Each 690V MCC has a 690V-230V, single-phase control power transformer that feeds a distribution panel with single pole breakers, one breaker per MCC bucket. The 230V winding is floating ungrounded on four of the transformers and is grounded on two of them. One has the hot leg grounded so the control circuit is still energized when the CB is open. The two grounds appear to be unintentional, (haven't located them yet).
I told the electricians to find and fix the unintentional grounds and then ground the neutral side - the one not connected to the breakers.
Is there a good reason to leave the control power ungrounded? I couldn't come up with one. BTW there is no ground detection circuit.