I'm looking at a lineup of 13.8kV double ended switchgear that is used as part of a co-generation arrangement. The swichgear has (2) 2000A main breakers which are connected to the utility transformers. The feeder breakers in this lineups serve various plant loads, and one feeder breaker on each side of the lineup is used as a generator bus interface breaker to a generator bus that is used as part of a co-generation scheme. The generators are actually 4.16kV so these 13.8kV interface breakers hit transformers before the 4.16kV generator bus.
In looking at this distribution arrangement I am curious what kind of typical protection schemes are provided for the 13.8kV switchger main breakers (utility interface breakers) and generator interface breakers. From looking at the one-line and control diagram it appears that the generator interface feeder breakers are supposed to have 50/51, 50/51N, 27/59, & 80O/U protection while the main utility interface breakers only appear to call for 67 and 67N direction protection.
My question is wheather or not this is typical for a co-generation arrangment? Do the main breakers only require 67/67N protection and not any 50/51N protection? If this is true I'd be interested in understanding why? There is relay on the main breakers that is capable of providing 50/51 functions, should these be used as backup protection?
I am simply looking at an existing drawing trying to understand the logic behind this type of protection scheme for my own interest. I appreciate any input others can offer.
Also I am curious if anyone has ever seen "CSR" and "TSR" relays in a DC breaker control schematic? I have never seen these before and from what I can tell from searching these appear to be some sort of single shot reclose relay used for the main breakers? Has anyone seen this before? I can post a schematic to further clarify.
Thanks for the help!
In looking at this distribution arrangement I am curious what kind of typical protection schemes are provided for the 13.8kV switchger main breakers (utility interface breakers) and generator interface breakers. From looking at the one-line and control diagram it appears that the generator interface feeder breakers are supposed to have 50/51, 50/51N, 27/59, & 80O/U protection while the main utility interface breakers only appear to call for 67 and 67N direction protection.
My question is wheather or not this is typical for a co-generation arrangment? Do the main breakers only require 67/67N protection and not any 50/51N protection? If this is true I'd be interested in understanding why? There is relay on the main breakers that is capable of providing 50/51 functions, should these be used as backup protection?
I am simply looking at an existing drawing trying to understand the logic behind this type of protection scheme for my own interest. I appreciate any input others can offer.
Also I am curious if anyone has ever seen "CSR" and "TSR" relays in a DC breaker control schematic? I have never seen these before and from what I can tell from searching these appear to be some sort of single shot reclose relay used for the main breakers? Has anyone seen this before? I can post a schematic to further clarify.
Thanks for the help!