CMU Control Joints 1

Status
Not open for further replies.

tft2001

Civil/Environmental
May 10, 2009
34
Are control joint spacing requirements the same for interior walls as for exterior walls?
 
Replies continue below

Recommended for you

According to some NCMA guidelines I've seen in the past, the interior wall joint spacing can be somewhat larger due to a smaller variation in thermal temperatures and also humidity changes.

In my area, we typically see 24 ft. exterior spacing and 32 ft to 36 ft interior.

 
Here is a link to get the NCMA Teks bulletins. Look in Chapter 10 for NCMA Tek 10-02C and also NCMA Tek 10-03

NCMA Teks



 