I have a situation with (4) 2000A, 480V closed transition switches with (2) ASCO and (2) Russelectrics. They are fed from a 6MW, 480V grounded wye generator plant. The utility has (4) 1500kVA delta grounded wye connected in a spot network.
The situation arose when the secondary spot network tripped on instantaneous current which is set at %50.
Thoughts. Generators typically have a little higher voltage and operate at a higher frequency to prevent reverse powering. So the ATS switches made a decision to perform a closed transition and there was a great enough difference that allowed the generators to provide power to the utility thus tripping the network protectors.
Solutions:
Ensure enough time delays are established between the transfer switches (even though it would be hard for them to close all at once - supposedly two closed at exactly the same time)
Add active sync controls that will coordinate the utilities voltage, frequency, phase angle and have a much tighter transition.
Add a sync check relay to each ATS that routes through the ATS controller which provides a permissive signal when these ATS's can perform the closed transition.
Tighten up the closed transition settings on the ATS
Obviously change all ATS's to an open transition
The situation arose when the secondary spot network tripped on instantaneous current which is set at %50.
Thoughts. Generators typically have a little higher voltage and operate at a higher frequency to prevent reverse powering. So the ATS switches made a decision to perform a closed transition and there was a great enough difference that allowed the generators to provide power to the utility thus tripping the network protectors.
Solutions:
Ensure enough time delays are established between the transfer switches (even though it would be hard for them to close all at once - supposedly two closed at exactly the same time)
Add active sync controls that will coordinate the utilities voltage, frequency, phase angle and have a much tighter transition.
Add a sync check relay to each ATS that routes through the ATS controller which provides a permissive signal when these ATS's can perform the closed transition.
Tighten up the closed transition settings on the ATS
Obviously change all ATS's to an open transition