bigwilly104
Mechanical
- Aug 31, 2006
- 15
I Have a system that is called a reheat hydronic system for building heating and cooling. It has a Laars 1million BTU boiler with a boiler loop pump. This drops onto a large loop with one grundfoss pump. The building has small coils throughout that heat air to diferant zones as needed. The problem is I am getting a large amount of solids in the system. They clog up my strainers at the coils and the main strainer on the roof. I also am loosing pump berings and seals way to fast. the water is running at 180 Deg. F. I have had the water tested by Nu-Calgon many times and they just suggest using their Ty-lon B20 treatment this is a Nitrite Borax corrosion inhibitor. I have treated as they suggested. The pumps are steal failing and I still have sollids in my strainers. there is very little steel in the system just the boiler, two pumps, the strainer, the air seperator, and the triple duty valve. The solid looks like flakey dirt when it first comes out wet, as it dries it becomes like a fine sand. Is there a way to get the solid tested to tell me if it is somthing that is coming in with the make up water. If I don't find a solution soon I will loose the contract this is a constant problem. Any advice would be nice.