Clean (electronoc) earth and plant earth bonding 1

Status
Not open for further replies.

sramesh

Mechanical
May 12, 2003
42
Request to get info on Standards / best practice on bonding of Clean earth grid and Plant safety earth grid. If both need to be bonded, type of bonding and preferred loacation of bonding? Your valuable input will be appreciated

Ramesh
 
Replies continue below

Recommended for you

The "clean" or "quiet" grounding concept has been largely discredited for the past twenty years or so.

Standards will depend on where you are at, which you don't bother to tell us.

Safety codes generally require that all grounding system be bonded together.

David Castor
 
Thanks David for your input. We are following IEC standard and there is a discussion on the grounding arrangement as our Instrumentation group requesting for separate grounding arrangement for their panels and not to connect it to general protective grounding grid.

Regards
Ramesh
 
Ramesh

They can't have that. Their panels are no different than other's and shall be connected to PE. Cable shields may have their own 'quiet' ground aka TE or some variation thereof.TE is always connected to PE. Usually in a star or tree fashion.

Or do they want to handle their I/O separately? I guess they are free to do whatever they want with them. Usually, a 4-20 mA loop isn't grounded anywhere.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 