Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Circuit breaker timing

Status
Not open for further replies.

thehoover

Electrical
Joined
Nov 18, 2002
Messages
5
Location
AU
Could anybody recommend an instrument for timing opening and closing of Medium voltage circuit breaker.
 
Programma makes a nice unit called the Egil.
This is especially well suited for MV breakers.
Others are designed for HV/EHV breakers and thus are more expensive.

call 847-506-1186 (US Sales Office)
 
Timing the opening and closing is one thing, a Time Travel Analysis is another. If you just need the amount of time it takes for the C/B to open or close after the function is initiated, you may not need the Time Travel Analysis device, which can be 'a lot of fun' to setup on the C/B, since it requires a mechanical connection on the C/B operating shaft to measure velocity and contact bounce.
 
Omicron CPC 100 is a multifunctional primary test system. Among other functions it can measure the opening/closing time of a breaker.
 

Basic stuff at netaworld/files/ItemFileA155.pdf.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top