A random wound 460 vac motor failed by turn to turn short. Only one phase and one coil was involved.
The failed coil happened to be a line-end coil, but 25% of coils in the machine are line end coil and steep voltage surges are not expected in this power system. So we ruled out surge as a cause.
The motor had been in service about 30 years service. During inspection, it was reported some parts of winding were dry and brittle, similar to what is expected after 30 years service.
Slides 1 and 2 show overview of endwinding and failure area.
Based on inspection, two different people opined two different apparent causes of the failure.
Scenario 1 - as highlighted in slide 3, the slot fill appears low. General looseness of winding from shrinkage and/or low initial slot fill are proposed as cause of failure. Note that in slide 4 the particular coil that failed does not have same appearance of low slot fill but it is postulated that this coil moved.
Scenario 2 - as highlighted in slide 5, the coils immediately bend as they exit the slot (rather than bending a little ways outside the slot). It is enough to distort the phase paper (which makes the looseness look worse than it really is from the end, even though it is admittedly loose looking). The cause of this early bend may be result of coil forming (the slot sections are not long enough, the end span is not long enough) and it also may be a result of winding assembly process (no attempt was made to establish a bend further outside the slot prior to dip/bake). Either way it places a tremendous stress on the coil in that area, which can be aggravated by thermal changes and vibration.
Among scenario 1 or 2, which seems more likely to you?
=====================================
(2B)+(2B)' ?
The failed coil happened to be a line-end coil, but 25% of coils in the machine are line end coil and steep voltage surges are not expected in this power system. So we ruled out surge as a cause.
The motor had been in service about 30 years service. During inspection, it was reported some parts of winding were dry and brittle, similar to what is expected after 30 years service.
Slides 1 and 2 show overview of endwinding and failure area.
Based on inspection, two different people opined two different apparent causes of the failure.
Scenario 1 - as highlighted in slide 3, the slot fill appears low. General looseness of winding from shrinkage and/or low initial slot fill are proposed as cause of failure. Note that in slide 4 the particular coil that failed does not have same appearance of low slot fill but it is postulated that this coil moved.
Scenario 2 - as highlighted in slide 5, the coils immediately bend as they exit the slot (rather than bending a little ways outside the slot). It is enough to distort the phase paper (which makes the looseness look worse than it really is from the end, even though it is admittedly loose looking). The cause of this early bend may be result of coil forming (the slot sections are not long enough, the end span is not long enough) and it also may be a result of winding assembly process (no attempt was made to establish a bend further outside the slot prior to dip/bake). Either way it places a tremendous stress on the coil in that area, which can be aggravated by thermal changes and vibration.
Among scenario 1 or 2, which seems more likely to you?
=====================================
(2B)+(2B)' ?