Secondary pump speeds should modulate in response to the remote secondary loop differential pressure signal. The set point will need to be refined after testing and balancing, but 10 psi is a typical starting point. The differential pressure signal is typically measuring the pressure difference between the chilled water supply and the chilled water return at the point in the secondary loop that has the greatest pressure loss between it and the secondary pumps.