Chilled Brine systems

Status
Not open for further replies.

scottguitreau

Chemical
Joined
Jun 14, 2005
Messages
3
Location
US
I am trying to find a way to check the chiller performance. It is an old style chiller that runs off its own PLC. Its coolant is freon and the cooling agent is a 50/50 methanol and water solution. Any ideas on the best way to test or determine its performance?
 
Scott:

The best and most practical way is to "put it through its paces": set it up to cool a measured and metered water flowrate, while measuring the electrical draw, coolant utilization, and all pertinent temperatures and pressures.

With the above data, I make a material and energy balance in an Excel Spreadsheet and find the refrigeration effect and the energy efficiency of the unit. This should tell you everything except for the durability or how long it will operate under these conditions. That, I'm afraid, is something you can only find out with a good case history of the unit or with a super inspection job prior to purchase. Otherwise, like all "used equipment surprises", you'll find out later - when you really need the unit's performance.

I recommend you read thread135-127098.

 