chiling unit refrigerant flowrate

Status
Not open for further replies.

alet

Mechanical
Joined
Oct 13, 2006
Messages
1
Location
IT
I have to install a chilling unit for cooling down a natural gas flowrate which can vary between 1,25 MSCM/day and 2,5 MSCM/day.

The choice can be: two complete chilling units with a 1,25 MSCM/day design; but, in order to save capex, could I use a single condenser, a single evaporator, and two compressors running single or in parallel, according to the refrigeration required by the gas flowrate?

the doubt is: would it be a problem if the refrigerant flowrate passing throught the evaporator and condenser cames from both the compressors or only from one, and therefore this flowrate is in a case double than in the other case?
would you envisage any other drawbacks in such a configuration?
thanks
 
No problem. We thought we had a problem when there were 4 compressors with 1 condensor and what appeared to be "blow-by" but I think we had a build up of noncondensibles in the refrigerant and cause the surge tank relief valve to go off.

The chiller doesn't care about how little refrigerant passes through it, if its a BEU. The gas should be able to turndown 50% on the tube side.
 