Solenoid pump (not valve) vs peristalic pump
the solenoid pump is the most common pump used for small hypo applications, inside is a plunger powered by the solenoid and a check valve on each side of the plunger. Life of the wearing materails is on the order of years. Once the offgasing issues are handled by proper suction tube design (short, vertical, straight) they are fairly trouble free. Suction lift is limited to 4 to 5 ft.
Brands include LMI, Pulsafeeder (Walace and Teirnan) and Prominet to name a few.
Peristalic pump move the fluid by pinching a tube in rollers. The life of the tube inside the rolllers is on the order of weeks. The tubing that has longer life is not compatable with hypo. While the suction lift issue is much greater the discharge pressure limits and tubing life are the drawbacks.
Maintenance on either pump requires messing with the hypo not a pleasent task.
As for the online analysis I have worked with two types
colormetric and amperometric
colormetric: (Hach and Hanna) a small sample is drawn and a dpd solution and buffer are added to the sample it is mixed the color read by a photo cell and lamp. Maintenance includes replacing the bottles once a month, cleaning the cell from once a week to once a year using acid dropper and q-tip and replacing the tubing once a year. Maintenance is heavy but regular and easy to diangonse. the process is visable and when something is wrong you can see the problem.
Since this device contains chemicals I install an air gap or rp backflow device on the sample supply just in case.
Amperometric (many brands and price ranges) water is flowed accross a probe, the magic box reads the level, sounds simple but when it is not working try cleaning the cell, or replacing the membrane, or repalce the fluid inside the memebrane, or replace the electrode. After any maintenace wait 4 hours then calibrate. Is it working? does the number match the grab sample? Maintenance is a guess and try this if not try that.
I prefer the hach colormetric.
As for sample location if it is known that there is little or no chlorine demand (biological, iron, maganese, hydrogen sulfide) sampling just after a bend will do the trick other wise sampling after 30 minutes is recomended i.e. figure flow rate and pipe diameter install tap way down there or after the storage tank. Static mixers are generally not required. If you are using a large storage tank I would sample before and after the tank and have either two analyzers or solenoid valves on a timer to switch the sample every hour or so.
Hope this helps