Change Set Pressure of PRV

Status
Not open for further replies.

PAN

Mechanical
Joined
Apr 25, 2001
Messages
549
Location
SG
I have an existing PRV with set pressure at ~24 barg. This valve will be relocated to install in the new location with lower design pressure (non-U stamp vessel). The required new set pressure is ~10 barg. Should we consider to reuse this valve? I would like to order the new valve for such location. However, the management team requirement is utilizing of the existing valve.

The calculated orifice area for the new location is closed to the existing valve. However, I never change the set pressure of PRV in this range. Please comment.
 
Collect the make, model number, serial number and any modifications that have been made to the PRV and call the vendor. They are the best ones to answer this question.

Good luck,
Latexman
 
Such a large set-pressure change will undoubtedly require a new spring for the valve. Latexman is right. Contact your vendor, or an ASME-approved repair facility certified for that brand of valve.
 
Thanks for the comment. I'm in process to contact the vendor.

In my understanding, after change the spring, both tightness test and pop test is necessary. If you have further comment, please inform me.
 