We have at least two sets of CCVT's that have gone into ferroresonant oscillations after a phase to ground fault. This occurs on breaker and one half configurations where (3) CCVT's are on a line as compared to radial where there is only (1) CCVT on a line.
The oscillations are peaking at about 138kV ph-gnd (1.7p.u.) on a 138kV system (normally 80kV to ground) which suggests maybe some type of ground potential rise?
Any experience with similar issues? Any suggestions on why the supression circuits do not seem to be effective (they are built into the CCVT's from the factory). This has hapened on 2 different manufacturers CCVT's.
The oscillations are peaking at about 138kV ph-gnd (1.7p.u.) on a 138kV system (normally 80kV to ground) which suggests maybe some type of ground potential rise?
Any experience with similar issues? Any suggestions on why the supression circuits do not seem to be effective (they are built into the CCVT's from the factory). This has hapened on 2 different manufacturers CCVT's.