Seats occasionally leak by. If you overpressure a trunnion boy cavity it will self relieve through the other seat. A PSV threaded into the body bleed port can prevent the self relieving if you just can't allow any flow all the way across the valve.
Set point is a big issue. It only takes a couple of psi of over pressure to lift the seat from the back. If you set the PSV at a couple of psi then it will lift every time you shut the valve.
Tough problem. You can solve it with a dP control valve that samples upstream and downstream and sends the lower pressure to the static side of a dP PSV which is set to lift when the cavitiy is 2-3 psid higher than the low pressure side of the Trunion. It sounds complicated, but it is pretty easy.
David