There are three cap banks (7800kVAR, 130 amps, 34.5kV) at a outdoor substation. The 34.5kV is hard neutral grounded at the transformer. They have an neutral unbalance relay that trips them off with an unbalance if the individual caps blow fuses.
Each cap bank is grounded through a PT (175/1), with the secondary of the PT's all paralleled inside the substation building going to a common over voltage relay.
The settings on the voltage relay are 8 volt to alarm and 15 volts trip with a 20-30 second delay.
My problem with this is that since the secondaries are all in parallel, wouldn't it take a lot of current on the secondary of the PT's to make the primary neutral match up on all three banks? There are no fuses on this.
Is this the proper way to do it or should there be a voltage imbalance relay for each?
Each cap bank is grounded through a PT (175/1), with the secondary of the PT's all paralleled inside the substation building going to a common over voltage relay.
The settings on the voltage relay are 8 volt to alarm and 15 volts trip with a 20-30 second delay.
My problem with this is that since the secondaries are all in parallel, wouldn't it take a lot of current on the secondary of the PT's to make the primary neutral match up on all three banks? There are no fuses on this.
Is this the proper way to do it or should there be a voltage imbalance relay for each?