capacitor bank for transformer test

Status
Not open for further replies.

Pafi

Electrical
Oct 21, 2002
40
Hello!
I would like to ask if someone knows anything about how the large - 100Mvar/ 6kV - capacitor bank used for high power transformer load test can be protected. It is a special case where this bank is used only for 5-6 hours at a time and only few times a year. Maybe someone is working in transformer producing companies where this method is used and knows more about this subject. I was thinking to divide it in several parts and use double star connection for each with unbalance relay.
Any comment is highly appreciated!
Thanks!
Pafi
 
Replies continue below

Recommended for you

Using a capacitor bank for transformer testing seems quite strange for me. However, for protection you can monitor:

- the difference in voltage between the midpoints of several branches (using series connection) in parallel

- the difference in current between different parallel branches

- as considered by yourself: the difference in starpoint voltage in a double star connection

In all cases the initial difference would be small and only a function of tolerances whereas a fault would cause a large difference.
 
Cap banks are sometimes used for the 180 hz. induced test, especially if it is a reactor.Usually the 180 hz. M-G sets are not large enough to handle this type of load.Cap banks are used to offset this high inductive loading factor.
 