I am sizing a feeder for a capacitor bank( 600V, 180KVar). Per Code, the size of breaker can be sized to be >1.35 rated current (173A). So I chosed 300A Circuit breaker. But I was told by the capacitor bank vendor, the RMS current( considering Harmonic and faults) is 265A. Though 300A is large enough, they prefer to choose 400A circuit breaker since the Maximum RMS current is 379A.
It is a filtered bank with some inductance. I can understand the RMS current is higher than the ratd current when the bank traps certain harmonic, but it should be limited by inductance. But 400A seems to be too high to me.