I am designing a Cantilevered Retaining Wall using the CRSI 2008 Manual as a reference. I have used the tables at the back of Chapter 14 as a starting point and do all the checks by hand. One comment I got from another engineer checking my work is that the vertical stem bars do not properly develop the ldh into the base slab. For example, if a #7 bar is specified for the stem flexural bars and these bars extend into the toe of the base, the base slab should be thick enough to develop ldh of the #7 before it turns into the toe. The CRSI manual does not seem to check this and their tables often specify bars that could not develop this length for the corresponding base thickness'.
I tried to rationalize with the checker that this bar is not really a 'hook' and that it is actually checked to fully develop beyond the face of the stem into the toe thus is actually being spliced into the base reinforcing.
Does anyone have an idea if the ldh really should be developed by these 'O' bars before the 90 degree turn into the toe or a good reason why its not necessary?
I tried to rationalize with the checker that this bar is not really a 'hook' and that it is actually checked to fully develop beyond the face of the stem into the toe thus is actually being spliced into the base reinforcing.
Does anyone have an idea if the ldh really should be developed by these 'O' bars before the 90 degree turn into the toe or a good reason why its not necessary?