I am calculating a pressure drop in a return duct system and have come across a fitting that does not have a Loss Coefficient listed in the SMACNA "HVAC Systems Duct Design". Refer to Figure 2-5 in the SMACNA "HVAC Duct Construction Standards Metal and Flexible" on page 2.7, titled "Divided Flow Branches", for an illustration of a similar fitting.
Two branch ducts (54"x36" and 42"x36") end with a 90° mitered elbow, which then converge to form one main duct (96"x36"). Assuming that the air flows through the 54”x36” duct and based on experience I would normally calculate:
1. the loss in the 54”x36” as a straight duct run (with the Branch Airflow).
2. the Loss Coefficient for a Mitered Elbow with Diverging Flow at the elbow.
3. the loss in the 96”x36” as a straight duct run (with the Total Airflow).
In the grand scheme of things the pressure loss may be minimal as compared to the total system pressure drop; however I am curious – “Would anyone calculate this differently?”