Calculating Wet Bulb Temperature using Air Temp RH and Pressure

Status
Not open for further replies.

ErrorFactor

Industrial
Joined
Aug 15, 2012
Messages
2
Location
US
thread724-129442

First compute dewpoint temperature (Td)
Td = (-430.22+237.7*LN(E))/(-LN(E)+19.08) = Td in °C
E = (rH/100)*0.611*EXP(17.27*T/(T+237.3))

Then compute wet bulb temperature (Tw)
Tw = [(GAMMA*T)+(DELTA*Td)]/(GAMMA+DELTA)
GAMMA = 0.00066*P
where P is ambient barometric pressure in kPa
DELTA = 4098*E/(Td+237.3)2

I've been trying to find the combined measurement uncertainty when using this formula, particularly the sensitivity coefficients. Thanks
 
Sensitivity coefficients?

Are you referring to the partial derivatives w.r.t. to particular parameters?

TTFN
faq731-376
7ofakss
 
So? You take the partial derivatives of the equation, in its unsimplified form.

TTFN
faq731-376
7ofakss
 