I have a cable tunnel which is 500m long and 2m x 2m cross-section. What's the air changes per hour to be considered for ventilation in normal mode and in smoke mode ?

HVAC68
 
For the normal mode, you need to calculate air quantity based on heat dissipation from cables(which is available based on watt/m).

For the smoke purge a velocity of 2.5 m/s is recommended across the tunnel cross section.Anything greater may impede escape from the tunnel.

I came across these figures while bidding for a cable tunnel project.

You would need to consult your local fire authority whether these figures can be used
 

Please check the above link which will give you some helpful guidelines.Looks like the figure I gave in previous post is wrong!

Arup recommends 5 m/s for smoke purge mode.

Also note that a cable cooling system is to be used(which is done with the help of a cooling tower circuit).These pipes are buried next to the cables in a sand trench.Therefore the ventilation system needs to remove only a portion of the heat generated by the cables.I can not remember what percentage I had apportioned for the cooling system .

A CFD model is required for the detailed design.


This could prove to be a lot trickier than you would have imagined!
 