For the normal mode, you need to calculate air quantity based on heat dissipation from cables(which is available based on watt/m).
For the smoke purge a velocity of 2.5 m/s is recommended across the tunnel cross section.Anything greater may impede escape from the tunnel.
I came across these figures while bidding for a cable tunnel project.
You would need to consult your local fire authority whether these figures can be used