arbil
Electrical
- Nov 2, 2008
- 17
For determining the cable size we are using the following formula
S= I*SQRT(t)/K , where
S= nominal cross sectional area of the conductor in mm2
I= Fault current in Amps
k= constant based on type of cable
t= short circuit withstand time in sec
My question is , whether there is any standard for deciding the value of 't' to be considered in the calculation . Normal practice for us is 1.0 sec for Incomer to HV switchboards , 0.6 sec for HV switchboards to plant feeder, and 0.2 sec for motor/transformer breaker feeder.But I don't have any backup for the same .
S= I*SQRT(t)/K , where
S= nominal cross sectional area of the conductor in mm2
I= Fault current in Amps
k= constant based on type of cable
t= short circuit withstand time in sec
My question is , whether there is any standard for deciding the value of 't' to be considered in the calculation . Normal practice for us is 1.0 sec for Incomer to HV switchboards , 0.6 sec for HV switchboards to plant feeder, and 0.2 sec for motor/transformer breaker feeder.But I don't have any backup for the same .