Cable derating

Status
Not open for further replies.

bartb102

Electrical
Nov 21, 2006
38
I'm trying to size power cables between switchgear and two generators. Each generator is rated 722A at 2400V. I want to use 2 500MCM MV90 conductors for each phase, 3 conductors in each of four conduits. If I arrange them 2h x 2w, cable is rated 344A, not enough. If I had only one generator and arranged them 1h x 2w the cable is rated 417A, great. Where to I find the rating for 1h x 4w? Or how far apart do the two banks of 1 x 2 conduits have to be to be considered separate banks?
Thanks,
Bart B
 
Replies continue below

Recommended for you

So, the total current = 2*720 A=1440 A and will be 4 cables per phase of 500 MCM copper MV90.
NEC art. 310.60 TABLE for Detail 2 indicate 375 A per conductor for 3 single core cable in an Electrical Duct.
From :INFORMATIVE ANNEX B
1) The factors of 0.88 for 2*Detail 1 and 0.94 for 4 conductor in Detail 2 there are for 0-2000 V cable only.
2) B.310.15(B)(2) Typical Applications Covered by Tables.
"where adjacent duct banks are used, a separation of 1.5 m (5 ft) between the centerlines of the closest ducts in each bank or 1.2 m (4 ft) between the extremities of the concrete envelopes is sufficient to prevent derating of the conductors due to mutual heating".
If you will calculate the permissible ampacity as per IEEE-835-1994 [SEE:art 310.60 Conductors Rated 2001 to 35,000 Volts. Informational Note No. 1] for MV90 cable [shield grounded only one end] you'll get 370 A per cable for 4 embedded ducts in a straight line keeping only 30" distance between the centerlines of closest ducts of 2 duct banks in the same conditions as per NEC:
30" depth; RHO=90; 7.5" distance between center lines in each bank of two; LF=100%;Earth ambient temp.20oC.
 
I assume these conduits are underground. Since you only need to supply 722 amps, you can use either 3 4/0 15 kv 90C @ 285 amps or
3 3/0 15 kv 90C @ 250 amps using detail 2 & 3 conduits per Table 310-60. 2 500 15 kv is not quite large enough.
 