bartb102
Electrical
- Nov 21, 2006
- 38
I'm trying to size power cables between switchgear and two generators. Each generator is rated 722A at 2400V. I want to use 2 500MCM MV90 conductors for each phase, 3 conductors in each of four conduits. If I arrange them 2h x 2w, cable is rated 344A, not enough. If I had only one generator and arranged them 1h x 2w the cable is rated 417A, great. Where to I find the rating for 1h x 4w? Or how far apart do the two banks of 1 x 2 conduits have to be to be considered separate banks?
Thanks,
Bart B
Thanks,
Bart B