I have this situation:
panelboard-bkr1
|
cable
|
|
bkr2
|
contactor
|
overload relay
|
motor
bkr2 is a magnetic-only MCP. (100A continuous, 150A frame)
motor is a 25hp induction machine (31A full load, 480V)
bkr2, contactor, and overload relay form a packaged stand-alone motor starter
I know that panelboard-bkr1 must be rated at a minum of 31A*1.25, and must protect cable while not tripping when motor starts due to current inrush.
overload relay is protecting the circuit from an overload, that is too much current drawn by motor. If bkr2 is opened, then cable cannot be 'overloaded'... it can only have a 'short circuit'.
My problem stems from having to use a 200A thermal-mag breaker for 'panelboard-bkr1' to allow motor inrush current without tripping... BUT I can't terminate cable rated for 200A at the 'bkr2'.
Is it allowable in this instance, per NEC, to use a cable rated for less than 200A, so long as 'panelboard-bkr1' protects the cable from short-circuit?
Thank you
panelboard-bkr1
|
cable
|
|
bkr2
|
contactor
|
overload relay
|
motor
bkr2 is a magnetic-only MCP. (100A continuous, 150A frame)
motor is a 25hp induction machine (31A full load, 480V)
bkr2, contactor, and overload relay form a packaged stand-alone motor starter
I know that panelboard-bkr1 must be rated at a minum of 31A*1.25, and must protect cable while not tripping when motor starts due to current inrush.
overload relay is protecting the circuit from an overload, that is too much current drawn by motor. If bkr2 is opened, then cable cannot be 'overloaded'... it can only have a 'short circuit'.
My problem stems from having to use a 200A thermal-mag breaker for 'panelboard-bkr1' to allow motor inrush current without tripping... BUT I can't terminate cable rated for 200A at the 'bkr2'.
Is it allowable in this instance, per NEC, to use a cable rated for less than 200A, so long as 'panelboard-bkr1' protects the cable from short-circuit?
Thank you