Our Transformer standard specifies that Bushing ampere rating shall be at least 20% higher than the respective transformer winding ampere rating at maximum transformer nameplate rating.
Does anybody have a basis for this standard? I checked c57.19 series on bushings but couldn’t find anything on this. Our vendor is committing to 19% over the LV winding ampere rating and we want to know if that is okay or not. The bushing in question is LV bushing – 25kV class, 150 kV BIL for a GSU transformer 25kV-230kV (750 MVA Transformer).
Thanks in advance.
Does anybody have a basis for this standard? I checked c57.19 series on bushings but couldn’t find anything on this. Our vendor is committing to 19% over the LV winding ampere rating and we want to know if that is okay or not. The bushing in question is LV bushing – 25kV class, 150 kV BIL for a GSU transformer 25kV-230kV (750 MVA Transformer).