jonathanwilkins
Civil/Environmental
- Mar 13, 2007
- 47
I've got an LVL (3-ply) supporting a large concentrated load...12,000# hanging into the side. The hanger will be a simpson hanger so no issues with that. I need to figure out the best way to connect the plies together of the supporting beam. Don't think the typical connection is sufficient. I've read through Breyer's book and don't believe he addresses this, I've also checked the NDS and they're fairly vague as well. What I'm pretty sure I need to do is be able to transfer, in single shear, 2/3 of the 12,000#. (1st ply will carry 1/3, the rear 2 plies the remaining). I come up with a lot of bolts. What's the best way to orient these bolts to reduce group action factor. Thanks.