As on a previous thread I'm building a new 400lb studio glass furnace to replace the current 100lb glass furnace.
Now going Moly elements
9 elements 9/18 312/500 60amp 12.5 volts each
wired in 3 series of 3each
40 kva transformer 4 to 1 step down
furnace will run on separate 200amp circuit
building has 400amps in single phase 240 to 248.8 volt It VARIES!!
I've been running checks on voltage to determine the build on the transformer...requested by the company I'm buying it from.
That's how I know that my voltage VARIES. The question I have is:
IS the following a problem:
This mornings Volt report:
Just a few lights on:
248.8 volts
100lb glass furnace temp. raised to engage elements:
244.3 volts
100lb furnace engaged and 15.5 amp compressor running:
242.3 volts
100lb furnace engaged and 15.5 amp compressor running and 30 amp kiln on: 240.6 volts
THEN add more lights and large fan: 240.2
Now going Moly elements
9 elements 9/18 312/500 60amp 12.5 volts each
wired in 3 series of 3each
40 kva transformer 4 to 1 step down
furnace will run on separate 200amp circuit
building has 400amps in single phase 240 to 248.8 volt It VARIES!!
I've been running checks on voltage to determine the build on the transformer...requested by the company I'm buying it from.
That's how I know that my voltage VARIES. The question I have is:
IS the following a problem:
This mornings Volt report:
Just a few lights on:
248.8 volts
100lb glass furnace temp. raised to engage elements:
244.3 volts
100lb furnace engaged and 15.5 amp compressor running:
242.3 volts
100lb furnace engaged and 15.5 amp compressor running and 30 amp kiln on: 240.6 volts
THEN add more lights and large fan: 240.2