- Oct 14, 2008
- 10
in 400 MVA transformer we get every night first stage alarm at , we noticed that the alarm comes when the ambient temperature is low and unit load is low. we susbect air ingress during low temperature time when both oil and air temperature are at thier lowest value.
we performed DGA for the oil and the result was as follow
Gas ppm
H2 82
O2 5980
N2 91848
CO2 8199
C2H4 Ethylene 38
C2H6 Ethane 185
C2H2 Acetylene 0
C3H8 & C3H6
Propane & Propene 183
CH4 Methane 149
CO Carbon Monoxide 1337
we are searching for any source of air ingress through leaking gaskets on the oil pipes and coolers.
Any feed back experience please. any available procedure
Thanks