H/600 is very stringent but that is common now. It is recommended by the BIA I believe and required by the UFC if you are doing government work. I used to use H/360.
Especially when the moisture resistant barrier is not 100% and the studs corrode where the screws pierced the galvanized studs. - Total rebuild possible in the future.
There is a problem when the veneer is more rigid than the back-up.
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.
The link Willis posted is interesting, and I agree with its conclusions. Brick veneer will always be stiffer than a stud backup, so the emphasis should be on protecting the studs and using corrosion resistant ties, preferably stainless steel.
Be carefule here, you guys are mixing two different criteria. The masonry code, ACI 530, provides deflection limits for horizontal (supporting beam) type deflections. It used to be L/600 or 0.3", and it is now just L/600. The criteria for maximum deflection of facade type veneer for designing the backup as discussed in this post is given in BIA tek note 28b (which I again disagree with per my post above but use because it is the current standard of care) which can be found here