Bottom plate failures at SWS tension chords

Status
Not open for further replies.

ChiefInspectorJeff

Structural
Nov 10, 2014
50
During inspections and plan review I have noticed the engineer allows 8" -12" from the corner holddown anchor bolts to the 2-2x4 chord of a wood SWS.
It seems the moment on the plate which is acting as a cantilever is much higher than designed for.Also the shear is higher than a 2x4 can take( especially on multistory buildings using type 1 SWS.)
Am I off base here? I recall these failures in testing.

Inspector Jeff
 
Replies continue below

Recommended for you

I don't do many wood frame shear walls, but that sounds suspicious. When specifically designing shear walls, I always pass by the mud sill with Strong-Tie HDU's or similar.



"It is imperative Cunth doesn't get his hands on those codes."
 
The Canadian code allows this for a certain range of load.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
I see this called out often, but I normally see an accompanying note adding a double stud adjacent to the holddown and providing edge nailing to the double stud.
 