What do you guys think for the classification of the boiler building. I give it a II at the worst case. It is a tricky one. Let me know what you think. Thank you.
 
Replies continue below

Recommended for you

The answer depends in part on what the boiler building is used for. If the boiler building served, say, a major hospital, the risk category would be high, probably Category IV. An identical boiler building serving, perhaps, a retail complex would be lower; likely Category II.

See ASCE 7-10 commentary C1.5.1 for a discussion on how to select the risk category.