Me again. I looked at a fan with nozzle outlet diameter of one meter. With flow of 10M3/sec, outlet velocity is 12.73M/s, air power is 972 watts. Assuming a fan dfficiency of 80%, shaft power is 1.215 kw.
For your purposes, you need a rather uniform velocity across the flow. This will neccesitate a fully developed axial flow fan with a well faired inlet, properly designed blades, and a good set of straightening vanes. The straighteners are not needed for energy recovery, but for flow uniformity. An egg crate straightener may also be needed. There may be other complications I have not thought of.