eit09

Civil/Environmental
Jul 8, 2009
183
I have a double angle veticle brace with one row of bolts connecting to a gusset plate. For block shear I use the formula from AISC 9th 0.3FuAv + 0.5FuAt.

In the case of 1 line a bolts I usually caclulate the available block shear strenght with At= 0. It has been braught to my attention that this is overly conservative and I need to acount for an At from the bolt to one edge of the gusset plate.

Is this correct, I should account for some At even though there is only one row of bolts? In all other calculations my At is the distance between the bolt rows.

 
Replies continue below

Recommended for you

Yes, At should be considered from bolt line to the nearest free perpendicular edge of the gusset plate. In the case of a long edge distance, one that could not possibly govern, I have used At = 0, but multiplied Av x 2. This assumes a "plowing out" of the gusset plate, failing along two lines of shear.
 
StrPE - that kind of failure is what the bearing and tearout limit states are for.
 
Connectegr,

For the case of two rows of bolts you are correct, but the condition for a verticle double angle at 45 deg with a single row of bolts connecting to a gusset is the case in question.
 