Hi,
We have a 69 kV isolated neutral station. There is two 69 kV transmission line that are ending at the station. One of them is very old and many fault occur. These fault are not always seen by protection because the system is unearthed and the line is quite long for 69 kV.
We have to had some equipment in the station and we are not sure about the BIL we should use. As per IEC 60071-1, for a 72,5 kV equipment, the standard BIl is 325 kV.
Our standard here is 350 kV BIL for 72,5 kV, but for solidly grounded system or low resistance grounded. Is this BIL is ok for unearthed system? We could easily use switch and CT with higher BIL, but for PT, it's a little bit complicated since standard PT with BIL higher will also have a higher ratio (they are for 120 kV system).
The MCOV (or Uc) of the surge arrester will be higher than 69 kV, probably around 72-74 kV.
Thanks a lot
We have a 69 kV isolated neutral station. There is two 69 kV transmission line that are ending at the station. One of them is very old and many fault occur. These fault are not always seen by protection because the system is unearthed and the line is quite long for 69 kV.
We have to had some equipment in the station and we are not sure about the BIL we should use. As per IEC 60071-1, for a 72,5 kV equipment, the standard BIl is 325 kV.
Our standard here is 350 kV BIL for 72,5 kV, but for solidly grounded system or low resistance grounded. Is this BIL is ok for unearthed system? We could easily use switch and CT with higher BIL, but for PT, it's a little bit complicated since standard PT with BIL higher will also have a higher ratio (they are for 120 kV system).
The MCOV (or Uc) of the surge arrester will be higher than 69 kV, probably around 72-74 kV.
Thanks a lot