cal91
Structural
- Apr 18, 2016
- 294
We frequently have buildings with multiple levels below grade. The seismic forces to apply to the below grade elements is a common topic of debate.
Do you use Sds / (R / Ie) ?
Or do you use Sds / (Ie) ?
To me it is rational to not include R; the seismic forces are delivered from the earth, and these levels will directly experience the ground accelerations. Any ductility / energy dissipation of the structure above will not reduce the accelerations experienced by the basement levels.
Others argue that it is overly conservative because ASCE 7 does not provide provisions stating to do as I suggest, and that there will be zero amplification of the accelerations, only attenuation. They argue to use R of the building, or at least 0.5*R.
What are your thoughts / experiences? Does anyone have pertinent literature or code references?
Thanks!
Do you use Sds / (R / Ie) ?
Or do you use Sds / (Ie) ?
To me it is rational to not include R; the seismic forces are delivered from the earth, and these levels will directly experience the ground accelerations. Any ductility / energy dissipation of the structure above will not reduce the accelerations experienced by the basement levels.
Others argue that it is overly conservative because ASCE 7 does not provide provisions stating to do as I suggest, and that there will be zero amplification of the accelerations, only attenuation. They argue to use R of the building, or at least 0.5*R.
What are your thoughts / experiences? Does anyone have pertinent literature or code references?
Thanks!