The approaches above which suggest checking vertical/moment and horizontal capacities separately will not provide reliable results under combined loading as those checks would provide the maximum capacity under just vertical or just horizontal loading. Shallow foundations have their vertical, horizontal, moment and torsional (VHMT) reactions all coupled; that's what defines them as shallow foundations. As such, you cannot reliably check capacity under combined VHMT loading without considering the effect of the other capacity components.
Applied M will affect the V capacity (i.e. effective area concept). T can be considered as an additional horizontal load/reduction to the H part of the capacity envelope. The remaining VH envelope is curved - not rectangular - which shows interaction between the V and H components. If you have combined loading, you need to check all of the capacities together.
Incidentally, for drained conditions, the VH envelope is defined by H/V (rather than H/Hmax) in some standards. Also, some standards recommend a drained sliding line to intercept the capacity envelope.