The battery area shall be ventilated, either by a natural or mechanical ventilation system, to prevent
accumulation of hydrogen. The ventilation system shall limit hydrogen accumulation to less than 2% of the
total volume of the battery area. The location should be free of areas that might collect pockets of hydrogen.
Maximum hydrogen evolution rate is 0.127 mL/s per charging ampere per cell at 25 °C and standard
pressure (760 mm Hg).8 The worst-case condition exists when forcing maximum current into a fully charged
battery.
A battery area that meets the above ventilation requirements should not be considered a classified
(hazardous) location;