jojolli
Structural
- Oct 9, 2001
- 3
I am designing a retaining wall which will rest on rock. The resultant eccentricity is required to be within the middle half of the footing. The calculated resultant is outside the middle third, but inside the middle half. This causes the bearing pressure q(min) to be negative in the equation
q=W/(B*L)[1-6e/L]
My understanding is this equation is only valid for e<L/6.
What is the proper bearing equation to use when the resultant falls outside the middle third, but inside the middle half?
q=W/(B*L)[1-6e/L]
My understanding is this equation is only valid for e<L/6.
What is the proper bearing equation to use when the resultant falls outside the middle third, but inside the middle half?