We have a new machine that came in. It has a 5ka rating. My available fault current is higher than that. I assume I need to install a disconnect and fuses to get it lower than the 5000. Anyone know what style or type of fuse I can use?
Why do you suggest an AHJ would need to approve this in regards to the acceptability of installing the panel at this location? It is simply lowering the "available fault current" as mentioned in 409.22.