Dumbo2929
Electrical
- May 31, 2005
- 109
I have a NEC question. We are installing a new electrical service and panel (outdoors) for a lighting project. The service is single-120/240V and is grounding at the service entrance (outdoor cabinet, panelboard, utility meter) via 2 ground rods. A grounding conductor is run with each branch feeder circuit to each light pole and the metal pole is bonded to the grounding conductor.
The local inspector says a auxilliary grounding electrode is required at each pole location. Is this correct? Section 250.54 in the 2008 NEC tells me if i install an auxilliary electrode to connect it to my system ground conductor, but not that is required. Does anyone know where this is required?
The local inspector says a auxilliary grounding electrode is required at each pole location. Is this correct? Section 250.54 in the 2008 NEC tells me if i install an auxilliary electrode to connect it to my system ground conductor, but not that is required. Does anyone know where this is required?