As per the title, I am struggling to find a clear answer on this one. I have found several sources that indicate how to determine the load that the solar panels are subject to, but I cannot find anywhere a clear answer as to what the existing roof structure is subject to, particularly addressing whether or not the roof structure is subject to additional uplift load due to the presence of the panels creating a pressure differential.
If you fastened something to a roof that was 10m above it (I know this is ridiculously far but it illustrates the point), then there would be two separate and independent instances of uplift load that you would need to add together. If a solar panel was directly fastened to the roof cladding with no gap, then I would confidently consider them as a single surface/skin and calculate uplift as per a standard roof scenario. I suspect there is a transition zone between the two where the effect of the panels changes relative to the separation distance, or something similar.
Does anyone have any advice, and even better any reference materials that discuss this?
The only documentation I have on this is the linked study which to my knowledge is what AS1170.2 AppD is based on. I can infer from this document that the forces from that appendix account for both the roof and the panel as that is how they were tested in the wind tunnel, but that is an inference, I don't know exactly how/where their load cells were located, and would therefore still love to hear others opinions and hopefully find something that is more explicit on this.
In case it is relevant I am in AUS, but understand this forum is NA based and am more than happy to look at NA documents or otherwise and make my own determination.
As per the title, I am struggling to find a clear answer on this one. I have found several sources that indicate how to determine the load that the solar panels are subject to, but I cannot find anywhere a clear answer as to what the existing roof structure is subject to, particularly addressing whether or not the roof structure is subject to additional uplift load due to the presence of the panels creating a pressure differential.
If you fastened something to a roof that was 10m above it (I know this is ridiculously far but it illustrates the point), then there would be two separate and independent instances of uplift load that you would need to add together. If a solar panel was directly fastened to the roof cladding with no gap, then I would confidently consider them as a single surface/skin and calculate uplift as per a standard roof scenario. I suspect there is a transition zone between the two where the effect of the panels changes relative to the separation distance, or something similar.
Does anyone have any advice, and even better any reference materials that discuss this?
The only documentation I have on this is the linked study which to my knowledge is what AS1170.2 AppD is based on. I can infer from this document that the forces from that appendix account for both the roof and the panel as that is how they were tested in the wind tunnel, but that is an inference, I don't know exactly how/where their load cells were located, and would therefore still love to hear others opinions and hopefully find something that is more explicit on this.
In case it is relevant I am in AUS, but understand this forum is NA based and am more than happy to look at NA documents or otherwise and make my own determination.