ridgeline

Civil/Environmental
May 29, 2008
28
I briefly looked in the ACI code to determine when to design for flecture in a shallow footing but havent found anything as of yet.

I would imagine you would begin adding flectural reinforcement when a minimum moment or stress is reached..

Any guidence would be appreciated. Thanks.
 
Replies continue below

Recommended for you

Try looking up Poulos and Davis' book on Elastic Solutions for Soil and Rock Mechanics. Section 12 on raft foundations. As example: The differential (say of circular footing) deflection of edge to centre depends on the relative flexibility of the slab - they given an equation (12.18). It appears that contact pressure is "uniform" as one would expect under a rigid foundation when the relative flexibility value is approximately 10. It is flexible say for values of about 0.5 or smaller with intermediaries of not really rigid - nor flexible in between.
K = [E(ftg)/E(soil)]*(1-mu(soil)^2)*[raft thickness/raft radius]^3.
Someone recently gave a download site for the book - I've found it again:
 
Footings may be designed for "Plain Concrete" provisions of ACI 318, (Chapter 22) as long as the moment is below a certain point. Once you violate that, you must consider the moment per Chapter 15.

 
The OP meant "flexure" when he spelled it "flecture", which I imagine led to BigH's answer about "flexibility". Language and spelling are important in our work as engineers.
 
In more active seismic regions, a minimum degree of flexural reinfoecing is required, regardless of the moment seen by the footing.

Mike McCann
MMC Engineering
 
I always throw some in, just to feel better.

;]

Seriously, concrete likes to crack.
 
I always check it as JAE noted...we don't do many plain concrete footings anymore, so it is a consideration for anything beyond a cube!
 