ASME VIII safety valves in an ASME I constructed power boiler

Status
Not open for further replies.

ashaari

Mechanical
Joined
Dec 17, 2008
Messages
30
Location
US
Dear all,

Can we install ASME VIII safety valves in an ASME I constructed power boiler?

I'm commissioning an ASME I power boiler and our safety valve manufacturer have difficulty in achieving re-seat 4% below set pressure. The best we achieve so far is 7% below set pressure, and now the debate is that the safety valves are at least meeting ASME VIII requirement, hence seeking a compromise to accept the valves. Just fyi, the 7% below set pressure is still above our max operating temp.

Thanks for your help!
 
How could the manufacturer have difficulties achieving 4% blowdown? It's either an ASME I certified safety valve or it's not. If you asked for an ASME I certified valve and the manufacturer delivered an ASME VIII I would expect them to replace it. What kind of valve are we talking about here, does it meet the 3% criteria (certified capacity at 3% above set pressure)?
 
It meets the 3% above set pressure criteria with ease. But yes, we're demanding the manufacturer to replace the safety valves to replace since it doesn't meet our requirement. I just wanted to double check if there is such thing as ASME VIII PSV in an ASME I boiler, because I have not heard of it before. Thanks!
 