Dear all,
Can we install ASME VIII safety valves in an ASME I constructed power boiler?
I'm commissioning an ASME I power boiler and our safety valve manufacturer have difficulty in achieving re-seat 4% below set pressure. The best we achieve so far is 7% below set pressure, and now the debate is that the safety valves are at least meeting ASME VIII requirement, hence seeking a compromise to accept the valves. Just fyi, the 7% below set pressure is still above our max operating temp.
Thanks for your help!
Can we install ASME VIII safety valves in an ASME I constructed power boiler?
I'm commissioning an ASME I power boiler and our safety valve manufacturer have difficulty in achieving re-seat 4% below set pressure. The best we achieve so far is 7% below set pressure, and now the debate is that the safety valves are at least meeting ASME VIII requirement, hence seeking a compromise to accept the valves. Just fyi, the 7% below set pressure is still above our max operating temp.