If you have a B31.3 piping system (e.g. 100 psig nitrogen) and a UV stamped PSV immediately downstream of a pressure regulator used to limit the maximum downstream pressure in a failed open scenario, all downstream users/vessels have their own adequately sized and installed pressure relief devices, and your piping system is built to contain the maximum possible pressure (and therefore does not need relief device protection):
1. What overpressure do you use for sizing the orifice?
2. What overpressure do you use for sizing the inlet/outlet piping?
Since this is not a required valve for vessel or piping overpressure protection, are you still beholden to the 10% overpressure just because the PSV is ASME stamped even though there's no Code requirement (i.e. the PSV could be removed)? Section VIII, I believe the non-mandatory?, says the piping should be sized at stamped rated flow (10% overpressure) but where does it say that if the valve is not required by Code does it need to be sized with overpressure?
This all came about as we were debating if it should be conservatively sized for 0% overpressure if, say, you had some downstream API 650/620 tanks. And if you did, would then the piping be sized to the proportional rated flow at 0% overpressure?
Thanks again
1. What overpressure do you use for sizing the orifice?
2. What overpressure do you use for sizing the inlet/outlet piping?
Since this is not a required valve for vessel or piping overpressure protection, are you still beholden to the 10% overpressure just because the PSV is ASME stamped even though there's no Code requirement (i.e. the PSV could be removed)? Section VIII, I believe the non-mandatory?, says the piping should be sized at stamped rated flow (10% overpressure) but where does it say that if the valve is not required by Code does it need to be sized with overpressure?
This all came about as we were debating if it should be conservatively sized for 0% overpressure if, say, you had some downstream API 650/620 tanks. And if you did, would then the piping be sized to the proportional rated flow at 0% overpressure?
Thanks again