ASHRAE Hospital Design 100% Ingres & Egress of O.A

Status
Not open for further replies.

onlinework

Mechanical
Joined
Mar 2, 2012
Messages
5
Location
KW
Dear et al!

According to ASHRAE Hospital design minimum outdoor air requirment for the healthcare fascilities. like ICU, 100% Outdoor air is recommended. Instead of All air exhausted to outdoor, it implies to Dash (-). What does it mean?. Is it optional to exhaust or recirculate with HEPA filter?.

Please comment

Regards
Himayath100
 
HEPA'd return, 16 ACH, with 4 ACH OA is the ASHRAE standard.
 